Generator cutting out when loaded

DesmoHyper

RIP John, we miss you
This question is for any sparks out there and probably @AirCon as I value his knowledge quite highly in the electric/ heating department.
I have a Honda generator in France that I use for my cement mixer, nail gun, circular saw and what not. There is no writing on the generator so I don’t know what it’s capabilities are. It has 110 and 240 volt outputs.
when I use a few high draw appliances like coMpressor Or starting my fucking massive table saw it cuts out due to the initial load being to high.. ( I assume)
Is there a resistor or capacitor or summit that I can add to it relatively simply to stop this or shall I just buy a new generator.
there is no mains electricity in some of the areas I work.
I don’t mean for this to turn in to a massive conversation like the Fischer heater one as I am genuinely asking a question and am not baiting an argument xx

hit me back just a chat your biggest fan.. Stan
 
This question is for any sparks out there and probably @AirCon as I value his knowledge quite highly in the electric/ heating department.
I have a Honda generator in France that I use for my cement mixer, nail gun, circular saw and what not. There is no writing on the generator so I don’t know what it’s capabilities are. It has 110 and 240 volt outputs.
when I use a few high draw appliances like coMpressor Or starting my fucking massive table saw it cuts out due to the initial load being to high.. ( I assume)
Is there a resistor or capacitor or summit that I can add to it relatively simply to stop this or shall I just buy a new generator.
there is no mains electricity in some of the areas I work.
I don’t mean for this to turn in to a massive conversation like the Fischer heater one as I am genuinely asking a question and am not baiting an argument xx

hit me back just a chat your biggest fan.. Stan
The initial current demand of a big saw or any motor without inverter control is huge.
Roughly you'll get around 600-700W of power per HP of the motor, assuming normal efficiencies.
Have you thought about adding inverter control to the big table saw?

It sounds like a new / bigger generator would be better.
 
The initial current demand of a big saw or any motor without inverter control is huge.
Roughly you'll get around 600-700W of power per HP of the motor, assuming normal efficiencies.
Have you thought about adding inverter control to the big table saw?

It sounds like a new / bigger generator would be better.
I haven’t really thought about doing anything to the appliances as that would mean my mixer, saws, compressor etc would all have to be modified I assume?
I shall wait til I’m back then and just buy a big fuck off generator. Shame really as I liked my little Honda.
Cheers and I knew you’d know 👍
 
Your compressor should start unloaded to minimise initial current, but it will still surge, if the generator used to start these things ok but now struggles it could be as simple as air filters, otherwise a bigger generator is probably in order. 👍
 
I used to have a generator to run a refrigerated display trailer for my market stalls. Had to run it on full power output to generate enough ooomph to start the electric motor that ran the fridge compressor. Once the fridge was running I could turn the generator down to its low output setting again. If it was left on it's low output setting then when the motor of the fridge demanded electricity to start it would just make a clicking noise as there wasn't enough power to start the motor - the genny would never stop or cut out it just wasn't providing enough power ton low output o start the electric motor of the fridge unit.

Someone told me, and @AirCon can confirm or not, that the genny needs to put out 4x as much power as a device with an electric motor, like the ones you use, is rated at in order to be big enough to provide the initial boost an electric motor needs.

Running a kettle (or a Fischer) off a genny is different, it needs 2500w so it draws 2500w. An electric motor rated at 1000w may need 4Kw to start.
 
Your compressor should start unloaded to minimise initial current, but it will still surge, if the generator used to start these things ok but now struggles it could be as simple as air filters, otherwise a bigger generator is probably in order. 👍
This generator was only ever used for small jobs before like Brad nailing and charging batteries but now I’m using it more in France I’ve noticed it more and more struggling with initial loads.
what’s the scoop with generator sizes then do I just order the most expensive one that will be portable by hand or is got to be a specific type for big loads or “hard ons” as my wife calls them 😂
 
I used to have a generator to run a refrigerated display trailer for my market stalls. Had to run it on full power output to generate enough ooomph to start the electric motor that ran the fridge compressor. Once the fridge was running I could turn the generator down to its low output setting again. If it was left on it's low output setting then when the motor of the fridge demanded electricity to start it would just make a clicking noise as there wasn't enough power to start the motor - the genny would never stop or cut out it just wasn't providing enough power ton low output o start the electric motor of the fridge unit.

Someone told me, and @AirCon can confirm or not, that the genny needs to put out 4x as much power as a device with an electric motor, like the ones you use, is rated at in order to be big enough to provide the initial boost an electric motor needs.

Running a kettle (or a Fischer) off a genny is different, it needs 2500w so it draws 2500w. An electric motor rated at 1000w may need 4Kw to start.
I turn her up to full whack and she still kills the engine. It has a variable throttle on it so apparently it speeds up when it feels a load which it does on the odd occasion I get it to keep running by squirting Easy start at the air filter 😆 . The motor on the gennie is fine but the load kills it dead.
We had a power cut the other day in France so I just wired a plug on it and plugged it in to the house and it powered everything fine, even the induction range works ok. I did kill the master switch though so that I wasn’t back powering the grid.dangerous I know but then I do like to live on the edge 😂
 
This generator was only ever used for small jobs before like Brad nailing and charging batteries but now I’m using it more in France I’ve noticed it more and more struggling with initial loads.
what’s the scoop with generator sizes then do I just order the most expensive one that will be portable by hand or is got to be a specific type for big loads or “hard ons” as my wife calls them 😂
You need to know what the max load the genny will see, so if you are running loads of stuff and try to start a big load that would be your worst case. For big loads you should have info on starting current so you can do the sums then buy a genny rated above your worst case. If you start your biggest load first you will be able to go with a slightly smaller genny if you need it more portable 👍
 
I used to have a generator to run a refrigerated display trailer for my market stalls. Had to run it on full power output to generate enough ooomph to start the electric motor that ran the fridge compressor. Once the fridge was running I could turn the generator down to its low output setting again. If it was left on it's low output setting then when the motor of the fridge demanded electricity to start it would just make a clicking noise as there wasn't enough power to start the motor - the genny would never stop or cut out it just wasn't providing enough power ton low output o start the electric motor of the fridge unit.

Someone told me, and @AirCon can confirm or not, that the genny needs to put out 4x as much power as a device with an electric motor, like the ones you use, is rated at in order to be big enough to provide the initial boost an electric motor needs.

Running a kettle (or a Fischer) off a genny is different, it needs 2500w so it draws 2500w. An electric motor rated at 1000w may need 4Kw to start.
As DesmoHyper says for his Children catcher, sorry Ice Cream wagon the voltage drop can mean the motor is unable to start.
A lot depends on the motor wiring/configuration/type (induction) and how sophisticated the generator is.

Do you have a picture of the Honda?

""Roughly 1kW of Genny per 1HP of electric motor you want to start""

Sizing Generators for Motor Starting​

Remember, an on-site engine/generator set is a limited source of power, both in horsepower available from the engine and kVA available from the generator. As such, it must be large enough to start as well as run connected motor loads.

We all know that motors draw a high inrush current during starting:typically six times full load current. But, inrush currents for the high-efficient motors specified today are almost double that amount. Motors with high inertia loads can also require up to three times rated power during starting.

Yes, it's common for motor starting kVA requirements to determine the size of the set. However, the following factors also play a key role in sizing gen-sets:

  • Harmonics caused by variable frequency drives.
  • Use of high-efficiency motors.
  • Sequential starting of motors.
What's involved. When starting motors, large voltage and frequency dips may occur if the generator set isn't sized properly. Other loads connected to the generator output may be more sensitive to voltage and frequency dips than the motor or motor starter, and this may cause problems. For example, a rate of change greater than 1 Hz/sec in generator frequency may cause some static UPS units to malfunction.
If the load on the generator set is a single large motor, particularly one requiring high starting torque, a number of problems can occur. They include: sustained low-voltage operation that can cause overheating; extended load acceleration times; opening of circuit breakers or motor protective devices; engine-generator protection shutdowns; and more.
Your gen-set's ability to start large motors without excessive voltage and frequency dip is a function of the complete system. This includes:

  • The engine power available;
  • The generator's capacity;
  • The response of the generator excitation system;
  • The energy stored in the rotating inertia of the gen-set; and
  • The acceleration of the motor and its load.
You must consider all these factors for proper gen-set sizing. Here's a simple rule for estimating the size of an engine-generator set for motor starting: 1kW of generator set rating per each 3/4 to 1 hp of motor nameplate.

Let's look more closely at a motor start. Induction motors have typical starting characteristics. The curve of motor current versus speed shows that during starting, the motor draws approximately six times its full load current; this current remains high until the motor reaches about 80% of speed. This high inrush current causes a dip in generator voltage. The electric power initially required by the motor (with the motor at standstill) is about 150% of rated power. The power required by the motor peaks at about 300% of rated power and 80% of speed with full voltage applied. But, the generator set supplies less than 300% power because starting voltage is lower than full voltage during acceleration, and because the generator set's rotating inertia transfers energy to the motor.

The motor must develop greater torque than required by the load. The motor's torque curve at full voltage is above the load's torque curve. The difference between the torque developed by motor and the torque required by the load determines the rate of acceleration. Since torque is proportional to voltage, any reduction in voltage means a proportional reduction in torque.

A properly sized generator set will support the high starting kVA requirements of the motor, and maintain sufficient output voltage for the motor, so it can develop adequate torque to accelerate the load to rated speed.

All standby gen-sets use synchronous generators with exciters. Many are available with permanent magnet generator (PMG) excitation systems. The PMG provides excitation power independent of the generator terminal voltage. As such, it can maintain full excitation:even during transient loading, such as motor starting. Full excitation power results in a less extensive voltage dip and improved recovery times.

Using reduced-voltage starting. Though a voltage dip often causes various problems, a controlled reduction in voltage at motor terminals can be beneficial, but only when reduction in motor torque is acceptable. Reducing motor starting kVA can reduce the required size of the gen-set, reduce the voltage dip, and provide a softer start for the motor loads. When sizing gen-sets, you must first determine the acceptable level of motor torque required during starting, or the loads will accelerate slowly, or even fail to reach full speed:ultimately causing motor damage.

Using solid-state starters. Solid-state starters can adjust the starting torque, acceleration ramp time, and current limit for controlled acceleration of a motor when it starts. For the purpose of sizing a gen-set, the current limit adjustment reduces the inrush current and may be used to reduce the starting kW and kVA requirement on the generator. The range of available current limit settings is typically from 150% to 600% of full-load current. A 600% current limit setting on the solid-state starter results in a gen-set sizing that's the same as an across-the-line starting. A 300% current limit setting reduces starting kVA by 50%.

Use of the current limit setting also reduces motor torque available to the load. From a gen-set sizing perspective, an extended acceleration ramp time and low current limit setting (if appropriate for the motor and the mechanical load) would result in the least voltage and frequency excursions.

One downside to using solid-state motor starters is their integral SCRs (silicon-controlled rectifiers) will cause voltage distortion. To compensate, you'll have to oversize the generator. The recommendation: two times the running kW load, except where you're using an automatic bypass. If the solid-state starter does have an automatic bypass, the SCRs are only in the circuit during starting. Once the motor is running, the bypass contactor closes and shunts the SCRs. In this case, you can ignore the voltage distortion during starting, and you don't have to add generator capacity.


FFS --- I've had to cut this down three times to allow me to post this.
 
Last edited:
I turn her up to full whack and she still kills the engine. It has a variable throttle on it so apparently it speeds up when it feels a load which it does on the odd occasion I get it to keep running by squirting Easy start at the air filter 😆 . The motor on the gennie is fine but the load kills it dead.
We had a power cut the other day in France so I just wired a plug on it and plugged it in to the house and it powered everything fine, even the induction range works ok. I did kill the master switch though so that I wasn’t back powering the grid.dangerous I know but then I do like to live on the edge 😂
I mate of mine likes to test the impedance (AC resistance) of the National Grid on a regular basis.
It's shocking I tell you....... boom tish
1605016083690.webp
1605016098912.webp
 
I haven’t really thought about doing anything to the appliances as that would mean my mixer, saws, compressor etc would all have to be modified I assume?
I shall wait til I’m back then and just buy a big fuck off generator. Shame really as I liked my little Honda.
Cheers and I knew you’d know 👍
It was only the big SAW that would need / benefit from the Inverter drive... not sure you could use one on a compressor due to the mechanical load of the compressor moving parts.
May be if you could off load the compressor part while the motor gets to speed... but then you'd need a clutch?
 
Last edited:
Your compressor should start unloaded to minimise initial current, but it will still surge, if the generator used to start these things ok but now struggles it could be as simple as air filters, otherwise a bigger generator is probably in order. 👍
**A generator MUST be started without any electrical load**
 
It was only the big SAW that would need / benefit from the Inverter drive... not sure you could use one on a compressor due to the load.
May be if you could off load the compressor part while the motor gets to speed... but then you'd need a clutch.
Yeah it’s a bit of a conundrum but I don’t mind getting a new one I just liked my old one as it’s never been any trouble starting or running and is very frugal plus easy to lift in the van
 
Yeah it’s a bit of a conundrum but I don’t mind getting a new one I just liked my old one as it’s never been any trouble starting or running and is very frugal plus easy to lift in the van
I've three HONDA generators... lovely bit of kit, 2x 3.4kVA (2 man lift) and a cassette for the van.
Nice a quiet for vac'ing down. My pump makes more noise than the genny.
1605016575403.webp
 
**A generator MUST be started without any electrical load**
What I mean is the compressor will be mechanically unloaded on start up so the genny just spins up the motor and mechanical rotating parts on no load, there's still the starting surge current to deal with though
 
I sort of agree, however you'd need to fit a clutch or damage will occur if you instantaneously load the compressor to the rotating motor set up.
Usually it's done by a valve so no air load is on the machine, then the unloading valve shuts loading the compressor after the motors initial surge
 
Usually it's done by a valve so no air load is on the machine, then the unloading valve shuts loading the compressor after the motors initial surge
OK... I know F'all about compressors apart from the one's here.
1605022528698.webp
1605022630046.webp

Like the man in the orthopaedic shoes.... I stand corrected.
 
Last edited:
Also my mig or tig welder can be temperamental
About 25-30 years ago I was asked to investigate why a sophisticated alarm system would suffer interference from a Tig welder.
I was told it was just the alarm and nothing else.... I trotted off somewhere up ta North , may be near the Wash area.
When I got there I found something similar to this. Only it was a machine making Yacht masts.
Not only did it activate the alarm, it also reset the telephone system, turned off the lights and shut down most of the estate.
Funnily enough it also reset my oscilloscope every time it was fired up.
Un-clipping the keypad cable from the SWA feeding the machine cured the problem.

1605026465299.png
 
About 25-30 years ago I was asked to investigate why a sophisticated alarm system would suffer interference from a Tig welder.
I was told it was just the alarm and nothing else.... I trotted off somewhere up ta North , may be near the Wash area.
When I got there I found something similar to this. Only it was a machine making Yacht masts.
Not only did it activate the alarm, it also reset the telephone system, turned off the lights and shut down most of the estate.
Funnily enough it also reset my oscilloscope every time it was fired up.
Un-clipping the keypad cable from the SWA feeding the machine cured the problem.

View attachment 2460
That is weld porn
 